I don't see a UL listing on that data sheet and most AHJ's will NOT approve a product without a UL listing. I almost always use the 3M 15WB+.
 
Derik

This is going on wood that will be exposed,

And they want the wood look
 
It hasn't been tested to determine if it meets the definitions of Noncombustible or Limited Combustible. The fire tests referenced in the data sheet are for interior finish materials. We see this used all the time for decorative finishes.

It won't work for the application you described.
 
Thank you both

That has been my feeling since I saw the product awhile back.

It just keeps coming back.
 