Dear All,
Based on API 521 6th edition section 5.3.3, a common mode failure such as instrument air can have coincident opening of the emergency depressuring normally energized valves along with the pressure control valves installed across the plant which fail in open position upon loss of instrument air. I know that we can avoid the opening of the BDVs by providing sufficiently sized secured instrument air bottles. However, do we really have to consider or check the above case while designing the flare system? Will the basis of the fact that the starting pressure under the instrument air failure scenario would be relatively lower than the usual conservative basis of relief or emergency fire blowdown design calculations and hence the combined PCV + depressurization load would be hence covered? Do we also have to check the case of all PCVs opening simultaneously to flare across the entire plant?