I have this problem:
A customer has four drives installed in one section of his plant. They are made by a well-known manufacturer and identical drives perform flawlessly in other parts of the plant.
The power range is 390, 545, 615 and 765 kW and they are fed from a 690 V, 50 Hz IT grid with a 3.15 MVA 5.73 % DY11 transformer. Input rectifiers are thyristor controlled and keep the DC link at 930 V constant.
The problem: The fuses of the two larger drives blow infrequently. The "MTBB" seems to be about one month, but has been as short as two days.
Observations:
*The two drives never blow their fuses at the same time.
*There are no visible transients on the mains voltage (recorded with 16 kS/s and 12 bit resolution, no filter).
*Current rises from normal load current (around 300 A) to 5400 A in 3 milliseconds (same recorder) when the Silized fuses blow and current drops to zero in about 2 milliseconds.
*The arc guard (ABB) reacts about 4 milliseconds after the current starts to rise.
*What I said about "no transients" is not quite true; there is a 6 kHz ringing started by the thyristors in the input rectifier of the inverters. The amplitude of this ringing is about 100 Vp-p. But there are no "killer transients" on the three phases.
*The fault current has a 100 000 kA/s maximum rate of rise and that corresponds well to what can be expected with 3% line reactors.
*Traces of flash-overs can be seen on the thyristor heat sinks (disc thyristors, marks on bolt and heat sink). The flash length is about 8 mm. Which (in my thinking) corresponds to more than 10 kV.
*Other equipment on the same grid are not influenced.
My analysis:
I have excluded false triggering because the DC link voltage is already high and premature triggering cannot produce this kind of overcurrent.
There is no overvoltage on the line. Not recorded and not influencing other equipment.
The high voltage must be generated by something. What?
I would like to bounce this idea in the forum:
The holding current (Ih) of a normal thyristor in this size is something between 100 and 500 mA and the snubbers are sized to take care of the "snap-off voltage" when the current goes below Ih.
Now, if the 6 kHz ringing snaps the thyristor off prematurely - remember that these thyristors work against the DC link, which is a counter-EMF. What will happen? Say that it is turned off while line current is at 5 A. The magnetic energy in the line reactor will then be one hundred times the normal energy at turn off and that will take the voltage on the snubbers up to more than ten times the normal voltage (energy in capacitor plus voltage drop in series resistor).
If the thyristors can take this high voltage without damage, then there would certainly be a flash-over. Wouldn't it? The question is: Can a thyristor withstand 10 kV or more for the time needed to ignite an arc?* I have not been able to find any data on this.
I need an informed second opinion. Or even better: Have you had this problem? Is it described anywhere in literature?
* The snubbers are connected with rather long wires and I do not think that the inductance is optimal. The fast snap-off voltage is probably not absorbed by the snubbers.
A customer has four drives installed in one section of his plant. They are made by a well-known manufacturer and identical drives perform flawlessly in other parts of the plant.
The power range is 390, 545, 615 and 765 kW and they are fed from a 690 V, 50 Hz IT grid with a 3.15 MVA 5.73 % DY11 transformer. Input rectifiers are thyristor controlled and keep the DC link at 930 V constant.
The problem: The fuses of the two larger drives blow infrequently. The "MTBB" seems to be about one month, but has been as short as two days.
Observations:
*The two drives never blow their fuses at the same time.
*There are no visible transients on the mains voltage (recorded with 16 kS/s and 12 bit resolution, no filter).
*Current rises from normal load current (around 300 A) to 5400 A in 3 milliseconds (same recorder) when the Silized fuses blow and current drops to zero in about 2 milliseconds.
*The arc guard (ABB) reacts about 4 milliseconds after the current starts to rise.
*What I said about "no transients" is not quite true; there is a 6 kHz ringing started by the thyristors in the input rectifier of the inverters. The amplitude of this ringing is about 100 Vp-p. But there are no "killer transients" on the three phases.
*The fault current has a 100 000 kA/s maximum rate of rise and that corresponds well to what can be expected with 3% line reactors.
*Traces of flash-overs can be seen on the thyristor heat sinks (disc thyristors, marks on bolt and heat sink). The flash length is about 8 mm. Which (in my thinking) corresponds to more than 10 kV.
*Other equipment on the same grid are not influenced.
My analysis:
I have excluded false triggering because the DC link voltage is already high and premature triggering cannot produce this kind of overcurrent.
There is no overvoltage on the line. Not recorded and not influencing other equipment.
The high voltage must be generated by something. What?
I would like to bounce this idea in the forum:
The holding current (Ih) of a normal thyristor in this size is something between 100 and 500 mA and the snubbers are sized to take care of the "snap-off voltage" when the current goes below Ih.
Now, if the 6 kHz ringing snaps the thyristor off prematurely - remember that these thyristors work against the DC link, which is a counter-EMF. What will happen? Say that it is turned off while line current is at 5 A. The magnetic energy in the line reactor will then be one hundred times the normal energy at turn off and that will take the voltage on the snubbers up to more than ten times the normal voltage (energy in capacitor plus voltage drop in series resistor).
If the thyristors can take this high voltage without damage, then there would certainly be a flash-over. Wouldn't it? The question is: Can a thyristor withstand 10 kV or more for the time needed to ignite an arc?* I have not been able to find any data on this.
I need an informed second opinion. Or even better: Have you had this problem? Is it described anywhere in literature?
* The snubbers are connected with rather long wires and I do not think that the inductance is optimal. The fast snap-off voltage is probably not absorbed by the snubbers.