We are experiencing heavy overflashing problems on our 500kW slipring motors (WRIM) in our plant. The plant have a lot of conveyors, the drives on the conveyors varies between 1 to three drives per conveyor. There is no spesific drive or conveyor that gives no problems, it occur sporadicaly on all the drives. Sometimes some of the motors have no problems for a period of 5 years, other times it occurs every 2 months. All the motors have vapourmatic (liquid) starters with three steps, the last step shorting the rotor.
All the overflash faults is between the sliprings in the area where the brushes are situated.
My opinion:
1. Overflash is due to a high voltage
High voltages occur during:
a) Start-up
b) Open rotor condition during running condition (short-rotor contactor open)
c) Can a high rotor voltage occur while the motor is electrically stopped, but the are rotor still turning?
(contactors open on stator side and on rotor side, but motor is still turning)
We have found no evidence for (b), the contactors are controlled and monitored by a PLC.
2. High Humidity
Not an option in our case, it is warm and dry.
3. Dust
Dust can be a main course (Plant is very dusty) but we don't experience this problem on the smaller motors (200kW) and sometimes the 500kW motors work for 5 years.
4.Isolation material between sliprings
Is discussed with manufacturer, but it is been manufactured for 2x rotor Volts + 1000V and been tested. The Rotor voltage is 855V
5. Brushes?
We've asked the manufacturer to increase the distance between the rings for a larger gap and to clean carbondust easier - not implemented yet
Any other ideas?
Ralph
We are experiencing heavy overflashing problems on our 500kW slipring motors (WRIM) in our plant. The plant have a lot of conveyors, the drives on the conveyors varies between 1 to three drives per conveyor. There is no spesific drive or conveyor that gives no problems, it occur sporadicaly on all the drives. Sometimes some of the motors have no problems for a period of 5 years, other times it occurs every 2 months. All the motors have vapourmatic (liquid) starters with three steps, the last step shorting the rotor.
All the overflash faults is between the sliprings in the area where the brushes are situated.
My opinion:
1. Overflash is due to a high voltage
High voltages occur during:
a) Start-up
b) Open rotor condition during running condition (short-rotor contactor open)
c) Can a high rotor voltage occur while the motor is electrically stopped, but the are rotor still turning?
(contactors open on stator side and on rotor side, but motor is still turning)
We have found no evidence for (b), the contactors are controlled and monitored by a PLC.
2. High Humidity
Not an option in our case, it is warm and dry.
3. Dust
Dust can be a main course (Plant is very dusty) but we don't experience this problem on the smaller motors (200kW) and sometimes the 500kW motors work for 5 years.
4.Isolation material between sliprings
Is discussed with manufacturer, but it is been manufactured for 2x rotor Volts + 1000V and been tested. The Rotor voltage is 855V
5. Brushes?
We've asked the manufacturer to increase the distance between the rings for a larger gap and to clean carbondust easier - not implemented yet
Any other ideas?
Ralph