Hi All,
ACI 318 11.12.3.3 reads ....The spacing between adjacent stirrup legs in the first line of shear reinforcement shall not exceed 2d measured in a direction parallel to the column face. However, other building codes such as the Eurocode recommend a further limitation on the spacing of shear reinforcement measured along perimeter around the column on successive lines of shear reinforcement.
Noting the above,according to Eurocode and many other building codes, the orthogonal arrangement of stirrup shear reinforcement shown on ACI commentary is not acceptable . And to satisfy the Euro codes requirement one has to reinforce as shown on attached, which is very difficult to monitor on site.
Why is the requirement of these building codes different? Could you please shed some light on this.
Thanks.
ACI 318 11.12.3.3 reads ....The spacing between adjacent stirrup legs in the first line of shear reinforcement shall not exceed 2d measured in a direction parallel to the column face. However, other building codes such as the Eurocode recommend a further limitation on the spacing of shear reinforcement measured along perimeter around the column on successive lines of shear reinforcement.