Luizmi:
Your question is not specific as to what you propose and you seem to have the idea that you can resolve centrifugal pump noise and vibration with a “flexible” connection. Refer to thread407-94199 for a discussion on one type of flexible connection.
Flexible connections have absolutely no ability to eliminate or lessen pump noise. Their acoustical attenuation value is nil. So this reason would lead to a waste of money. Since you don’t state the origin of the noise and vibrations, I have to assume they originate in the pump. This is a bad installation/application/operation if that is so. Centrifugal pumps should make no noise nor have any vibrations. In fact, the majority of centrifugal pumps that I have installed and operated in over 44 years have run so quietly that the coupling guards have had to be removed in order to see if the shaft coupling was rotating. And my installations have been typical of most others. A well-designed and applied centrifugal pump will generate no detectable noise or vibration. So something is wrong with your installation if that is occurring.
However, noise and vibration can be transmitted to a pump by upstream or downstream equipment. If this is the case, you have another type of problem that should be resolved first because it will affect the mechanical operation of the pump if allowed. No process equipment – outside of that expressly designed to vibrate (shaker screens, vibrators, etc.) – should be allowed to vibrate to the point where it affects critical equipment such as a pump. This is not proper engineering and there is no solution except to cure the cause – not the effect.
There are various types of “flexible” connections: bellows hoses, rubber hoses, omega loops, etc., etc.. You haven’t identified what type you are proposing. I would warn you that in the majority of cases the hose or flexible connection is weakest mechanical link in such a configuration. And in the case of bellows, the flexible connection is subject to a reduced life due to constant flexing.
If you are talking about a contractor’s portable pump skid, designed for mobility and temporary use, that is a different situation – especially if the fluid in question is benign (like water). But if this involves a serious, long-term installation in an industrial processing environment then vibration and noise effects should not be allowed to exist. Any hose or flexible connection you install as a “remedy” to the effects is subject to extensive stress and will fail with time. I am not opposed to flexible connections where needed, but in the case of operating pumps I would be very concerned about the cause (and hazards) of any produced noise and vibrations.
I do not believe that horsepower is a measure of the vibration/noise expected of a centrifugal pump. I am accustomed to a constant, steady “hum” of a centrifugal pump – but no vibration. Consequently, I find no justifiable reason for using flexible connections on process centrifugal pumps – suction or discharge. Perhaps you have other reasons for your proposal; if so, please indicate with specific details and information.
I hope this experience helps you.
Art Montemayor
Spring, TX