enginerding
Structural
- Oct 3, 2006
- 205
We are helping a fabricator with some connection design where the EOR simply provided drawings that specified "Steel fabricator shall provide full moment connection between all beams to columns with the design of full capacity of the section".
We were directed to provide field welded connections, so we designed connections with bolted shear tabs with CJP welds from beam flanges to column flanges or stiffeners in column webs, depending on the orientation of the connection.
This design was rejected by the EOR, and the EOR stated that they want Type 2 connections and pointed to page 4-100 of the 9th Ed. AISC Manual. (This requirement was not stated in the drawings or specs.)
I was under the impression that FMCs were used so that the connection could be designed for something less than the full moment capacity of the beam. Am I missing something? Doesn't it kind of miss the point when we have to provide the capacity of the full section?
According to AISC, FMC connections result in heavier beams, so my design moment, the "full capacity of the section," is even higher than it would be if the whole structure were designed with FR connections. Do I understand this correctly?
We were directed to provide field welded connections, so we designed connections with bolted shear tabs with CJP welds from beam flanges to column flanges or stiffeners in column webs, depending on the orientation of the connection.
This design was rejected by the EOR, and the EOR stated that they want Type 2 connections and pointed to page 4-100 of the 9th Ed. AISC Manual. (This requirement was not stated in the drawings or specs.)
I was under the impression that FMCs were used so that the connection could be designed for something less than the full moment capacity of the beam. Am I missing something? Doesn't it kind of miss the point when we have to provide the capacity of the full section?
According to AISC, FMC connections result in heavier beams, so my design moment, the "full capacity of the section," is even higher than it would be if the whole structure were designed with FR connections. Do I understand this correctly?