Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Floor Mounted Obstructions - Extra Hazard

Status
Not open for further replies.

Haldorson

Mechanical
Mar 27, 2011
92

In NFPA 13 (2010) Figure 8.6.5.2.2 describes floor mounted obstructions in LH occupancies only. Is there analogous rules for OH or EH occupancies with regards to floor mounted obstructions?
 
Replies continue below

Recommended for you

Short answer, no. Note that 8.6.5.2.2 ends at 18" below the deflector. Not coincidentally, this is where the obstruction rules for standard spray heads change. NFPA 13 2010 is giving a spacing credit for light hazard occupancies that doesn't extend to ordinary and extra hazard. Therefore, if the obstruction was 18" or closer to the deflector, you would treat it as a wall and space accordingly. If it was greater than 18" below the deflector, you would apply NFPA 13-2010 8.5.5.3. If your floor mounted obstruction doesn't fall into one of the "sprinkler required below" categories, then go on your merry way and space heads as if it didn't exist.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor