Morten,
Can I fairly answer your question?
Probably not. I don’t have a history of consistent use of one manufacturer to be able to say if they always perform one way or another. Because I design systems for use globally, I have used different manufacturers in different installations. Usually I choose the equipment type and then choose the manufacturer from the clients approved vendor list so that I don’t introduce “aliens” into their service and maintenance programs. All the pumps and VFDs, I have experience of, seem to have been trouble free especially once installed and commissioned. The problems I have had have been only with this last system and it would be unfair to infer either a distributor or manufacturer as being the source of the problem nor that it is typical.
This latest process viscosity measurement system was for a pipeline blending application for heavy fuel oil custom designed for a refinery in Siberia.
I use PD pumps and VFD control…my choice and for reasons similar to those given by MVD.
I don’t consider the energy costs as the main concern is serviceability. It is important to design systems with minimal downtime, minimal call for special skills and to cause minimum disruption to the end users existing service capability.
The point is that any energy savings might be more than consumed in down time and lost production if things go wrong. If things do go wrong then specialist support can come from the manufacturer or his distributor.
In this case equipment manufacturer choice was based on availability with appropriate approvals for import into Russia.
Fabricated in the UK, but to get all the necessary GOST hazardous area approvals and Russian language manuals, plus the GOST meterological certificate, the Russian agent had to organise all the key equipment item procurement in Moscow. This meant dealing with the Moscow distributors for suitable equipment.
Hence an Alweiller pump (with Siemens motor), with Siemens for the Micromaster VFD.
So much for choice.
Next, problem solving: –31C temperatures [A pipe side installation and for some reason, whether the Alberta oilfields or Siberian refineries (Southern Siberia, fortunately), I always seem to be supervising commissioning these systems in winter!] doesn’t make for an un-biased or balanced view I’m afraid.
Yes, I did have problems (I don’t usually when commissioning); none with the pump and some with the Micromaster, none with the Fisher Valves used for the heat exchanger services.
This means we had to get telephone support from the UK, Moscow, and Germany, all in different time zones and this is not a fair guide to the sort of support you might normally expect. It was less than I hoped for and probably better than I had a realistic right to expect.
The Alweiller pump works fine supplied with a Siemens motor and the Siemens Micromaster VFD, very well in fact.
Q: Would I use them again?
A: No reason not to. If I had found the same problems over and over again with any one supplier I could give you a better answer.
Q: Would I advise the client against any of the vendors specified for this system?
A: No. All work well now they are commissioned.
Q: Would I use VFD again?
A: absolutely.
My only recommendation is that if you choose Micromaster VFD, at the minimum, to get the BOP (Basic Operator Panel), a key-pad module that plugs into the micromaster. The price was £15. Why wasn’t this standard? Why wasn’t it offered? Is this usually not offered or was it just this distributor?
When doing the FATs , downloaded the Micromaster software from the web site, intending to use MODBUS to configure, it proved to be a huge program and we found had downloaded the wrong program. Why are/were they different for different sizes of Micromaster?
Then we couldn’t get the new program to operate over the old.
During commissioning when we returned to this as a programing method we and we found the programs no longer available for download! Was it something we did wrong? Don’t know. By that time we had a BOP sent down from Moscow so we commissioned with this keypad device and left it in place. This is a problem only if you want to be able to control the VFD remotely by comms and only if they don’t have a clean solution and I don’t know that they don’t. We had a problem and we moved to a different solution rather than try to solve the problem.
Sorry for the long answer.