Is there also a possibility of a flow induced pulsation on liquid lines past a dead leg branches along a pipeline sytem?
This seems only applicable for gas lines. Can anyone shed light on this matter?

Thanks in advance.

jim0210
 
Replies continue below

Recommended for you

Yes, it's possible. The dead leg acts as a 1/4-wave tube. Nat. frequency of the dead leg is reduced a bunch if there is trapped air in it.
 
branch connections do create a flow disturbance down stream, even if the branch is non-flowing. resonance problems occur if the turbulence created by the branch coinsid with an accoustic resonance condition
 
Yes, it's generally more common in gas systems, but it's also possible in liquid systems. Search the interwebz for Strouhal number or vortex shedding to figure out how to figure the vortex shedding frequency, and you can also calculate the branch connection stub acoustic natural frequency.
 
Hi All,

Thank you very much for all the replies.. Your inputs are highly appreciated..
Thanks again,

Jim0210
 