We are running a Gas/LNG plant here in Bioko island, and there is one interesting issue related to parallel pump operation and flow measurement/control from the day No.1 of plant operation. I have attached all the information I have in the Excel workbook uploaded below. It also includes a simple process model prepared in HYSYS, where all piping isometrics, pump curves (Q-H), and control valve data are incorporated. Model outputs match closely with actual performance data.
I would appreciate if you can take a look at these materials and help us figuring out the following issues:
1. Why there is such fluctuation of flow across the flow control valve in common discharge line, as compared to individual flows delivered by each pump? All flows are measured by Pitot tubes, both at individual pump discharge and in the common discharge line (upstream of FCV12002). You can see the range of fluctuations of the sum of flows from two pumps operating is much smaller than the fluctuations observed at the common FCV. The same thing happens when we close the FCV and control the flow through FCV bypass line - flow fluctuations remain at 150 m3/h! This indicates the control valve is definitely not the culprit of our problem, although it has been designed for much smaller dP than it is in practice. In addition, there is an offset of Pump (1) + Pump (2) flow versus total flow measured upstream of FCV.
2. The Instrument guys and us did some testing, and these are the results:
- Instrument maintenance checked out the flow transmitter FT12002 including blowing down the impulse lines.
- FC12002 in manual output steady, valve feedback fluctuating 0.5% (witnessed movement at valve), unsteady flow around 150 m3/hr.
- Flow controlled via bypass valve and FV12002 closed. No improvement.
- Flow controlled via bypass valve, FV12002 closed and upstream block valve of FV12002 closed. No improvement.
I would appreciate if you can take a look at these materials and help us figuring out the following issues:
1. Why there is such fluctuation of flow across the flow control valve in common discharge line, as compared to individual flows delivered by each pump? All flows are measured by Pitot tubes, both at individual pump discharge and in the common discharge line (upstream of FCV12002). You can see the range of fluctuations of the sum of flows from two pumps operating is much smaller than the fluctuations observed at the common FCV. The same thing happens when we close the FCV and control the flow through FCV bypass line - flow fluctuations remain at 150 m3/h! This indicates the control valve is definitely not the culprit of our problem, although it has been designed for much smaller dP than it is in practice. In addition, there is an offset of Pump (1) + Pump (2) flow versus total flow measured upstream of FCV.
2. The Instrument guys and us did some testing, and these are the results:
- Instrument maintenance checked out the flow transmitter FT12002 including blowing down the impulse lines.
- FC12002 in manual output steady, valve feedback fluctuating 0.5% (witnessed movement at valve), unsteady flow around 150 m3/hr.
- Flow controlled via bypass valve and FV12002 closed. No improvement.
- Flow controlled via bypass valve, FV12002 closed and upstream block valve of FV12002 closed. No improvement.