Flow Switch to detect Seal Water

Status
Not open for further replies.

BearB

Electrical
Jan 18, 2007
54
I need to install a flow switch to detect Seal Water to interlock the starting of a 2300v motor. Does anyone know of a product that they may have used in a simliar application?
 
Replies continue below

Recommended for you

We could help if enough data is presented. Is this a seal pot, vacuum break eqpt or what?
 
The seal is a mechanical seal, the rebuild kit is a graphite rope, that requires water to keep it from leaking. It is on a Hydra Pulper. That is all the information I have about the seal at this time.
 
BearB,
I have had many bad experiences with flow switches, in particular where they spend a long time in the activated position. When you need them to work, they are stuck closed. In a clean lube oil application I have seen 50% failure. For this reason I almost never buy flow switches and I will not recommend one.
If you have a situation where the flow shuts off when the motor stops at least make sure that the switch indicates low flow as a permissive to re-start. Some mechanical seals have a very low flow rate, you might also consider using a pressure switch (water pressure at seal).
If it's a critical application I would recommend using a flow or pressure transmitter or at least a flow switch operating on the principle of rotating paddle e.g. Signet.
Good luck
Roy (Instrumentation consultant)
 
Thanks for the feedback, this site is always helpful in many ways.
The application is a HydraPulper(grinds paper with water into pulp)does this with a 2300v motor connected to an agitator in the bottom of the vessel. There is a Seal at the propeller that needs constant water flow for positive pressure that prevents the pulp from entering. The flow is less than 5 GPM. The seal that is being used is a John Crane Split Mechanical 37FS. The issue we have is water is left off, valve handle gets closed on a repair and days later when the seal goes bad it is notice. This is very costly to replace. I think the best prevention would be an inspection sheet but I need to get cost and layout together before I present both.
 
Fit a position switch on the valve handle configured as either a start interlock or as a trip? We did this a few years ago on a 3750HP BFW pump, except it was a thrust bearing balance line which they kept leaving shut and which resulted in wiping out the thrust bearing. Now if the valve is shut then the pump won't run.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
If your only concern is that valve position, you could put on a limit switch that closes when the valve is open. I have done that many times, but mostly for indication not as interlock.

I have had bad luck with flow switches as Roy said, esp at those low rates. When I need a flow switch I always try to have a pressure switch as well.

I will look up my flow switch models when back in office Monday.
 
My favorite flow switches are made by ifm. Link below. I use SI-1000 series. They can learn what the normal flow rate is and can feed you a signal for hi (down stream leak) or low (upstream leak or valve closed) flow. Never had a reliability issue with these flow switches, but I do throw in a pressure switch as well.
 
 http://www.ifm.com/ifmca/web/padv02_10_10_10.htm