Flow velocity in fire mains 1

Status
Not open for further replies.

DPAJR

Civil/Environmental
Jul 8, 2006
74
My plumbing code lists 10 feet/sec as the maximum flow velocity in pipes for domestic water. I can't find a similar restriction in either the UFC or NFPA 24 for fire mains. Does anyone know if there is one?

Thanks,
DPAJR
 
Replies continue below

Recommended for you

NFPA 24 recommends a maximum velocity pressure of 10 PSIG. However, it is not a mandatory requirement because it is in the Annex, which contains recommendations rather than requirements.
 
stookeyfpe,

Thanks. I guess I missed it in NFPA 24. A star for you.

DPAJR
 