can you please help diagnostic the issue :
our platform running by 3 generators each sized 6.6kv 11kva ,2 running and one in standby controlled by load sharing system .
the normal power demand is about 6400kw , the load in 0.4kv level contains high power heaters that consume 1000kw per each (two heater units)and driven by VFC, the power consumption of each heating unit is in-stable it fluctuated by 300kw per less than second ,current harmonic 11 THD.
time to time a fluctuation in power between the two turbines cause nuisance shutdown .
for instance last shutdown :
1-Before shutdown unbalance occurred in power load suddenly increase in Turbine A from 3,478MW up to 5,116MW, and after decrease back to 3.478MW then increased again to 4.876MW see below photos with trends(the power load is the red line on trend):
2-After one second the power suddenly decreases in Turbine B from 3,272MW up to 2,316MW, to compensate load sharing see below photos with trends:
please see the trend of both :
TG-A:
note the reactive power for each turbin was totally shared the same : TG-A 1550 KVAR ,TG-B 1250KVAR
can you please help diagnostic the issue :
our platform running by 3 generators each sized 6.6kv 11kva ,2 running and one in standby controlled by load sharing system .
the normal power demand is about 6400kw , the load in 0.4kv level contains high power heaters that consume 1000kw per each (two heater units)and driven by VFC, the power consumption of each heating unit is in-stable it fluctuated by 300kw per less than second ,current harmonic 11 THD.
time to time a fluctuation in power between the two turbines cause nuisance shutdown .
for instance last shutdown :
1-Before shutdown unbalance occurred in power load suddenly increase in Turbine A from 3,478MW up to 5,116MW, and after decrease back to 3.478MW then increased again to 4.876MW see below photos with trends(the power load is the red line on trend):
2-After one second the power suddenly decreases in Turbine B from 3,272MW up to 2,316MW, to compensate load sharing see below photos with trends:
please see the trend of both :
TG-A:
https://files.engineering.com/getfile.aspx?folder=5b818d85-c0d2-43b8-998c-5b3ce48531ee&file=tg_a.jpg
TG-B https://files.engineering.com/getfile.aspx?folder=13412fae-2cff-4b56-ab81-82299563b671&file=tg_b.jpg
[/indentnote the reactive power for each turbin was totally shared the same : TG-A 1550 KVAR ,TG-B 1250KVAR