I would like to know if I need to change the fluke 435 default current Range 3000A to be close to load current or keep as is to start measurement as the manual suggest.
The panel I will connect has total load of 100A.
 
Replies continue below

Recommended for you

Thanks.
If you measure a panel with 3 phase 3 wire, which connection to be made? Delta or Y IT on the fluke.
I guess both should work.
 
Not really in this case.
I got Fluke Technical support recommendation to use Delta. I got feedback from experienced technician to use Y-IT.
 