I have a nasty situation that involves an existing warehouse that has Group A exposed, expanded plastic. The owner would rather shut down the operation than install in-rack sprinklers.
What I'm trying to do is determine whether there is a maximum storage height permitted given the existing ceiling sprinkler system.
Existing ceiling sprinkler system:
-ESFR pendents, 17 K, 100 sq.ft. spacing, designed to protect Class IV commodities to 25' in height at 35 psi per sprinkler.
NFPA 13 does not cover Group A exposed, expanded plastics. Therefore I have turned to FM Datasheet 8-9.
It appears to me the datasheet provides no relief at all for having lower storage heights. It appears to me that if you have a ceiling of 30' and are storing the commodity to 1', 5', 14', or 25' the requirements are equal. Is this true?
I would like to be able to provide some option for the owner, even if it means 5' solid-piles or 8' of open rack storage.
//