I have an older 200,000 sq ft warehouse which used standard response K=8.0 uprights and today they want to store plastic products.
FM Global wants Data Sheet 8-9 Table 10 and with the building height 35'-0" it appears we have a choice between 12 K22.4 @ 75 psi or 12 K25.2 @ 60 psi.
Yes, we are looking at a tank and 2,000 gpm pump because the city doesn't have enough water.
The building has 50' bays, 2'-6" open web steel joists (5'-0" OC) with 30" solid metal beams.
I can't find the requirement for baffles to separate the older SR and newer QR storage sprinklers and I know the baffle requirement details HAS to be somewhere.
If I remember right it used to be in 2.0 but I can't find it anywhere.
What I am thinking of doing is extending the area of application a little farther to the 30" steel beams and use them as the baffle.
And is the depth of the baffle 2'-0" or is it more? I seem to remember 2'-0" being the standard but I need to make darn sure.
There's a 2" open space above the beam and roof deck where the joists sits on the solid beam. I don't think that has to be sealed if I remember correctly.
Can anyone point to where I can find the requirements for baffles FM?
Yeah, fans have to be moved but this gives a good idea what we are dealing with.
FM Global wants Data Sheet 8-9 Table 10 and with the building height 35'-0" it appears we have a choice between 12 K22.4 @ 75 psi or 12 K25.2 @ 60 psi.
Yes, we are looking at a tank and 2,000 gpm pump because the city doesn't have enough water.
The building has 50' bays, 2'-6" open web steel joists (5'-0" OC) with 30" solid metal beams.
I can't find the requirement for baffles to separate the older SR and newer QR storage sprinklers and I know the baffle requirement details HAS to be somewhere.
If I remember right it used to be in 2.0 but I can't find it anywhere.
What I am thinking of doing is extending the area of application a little farther to the 30" steel beams and use them as the baffle.
And is the depth of the baffle 2'-0" or is it more? I seem to remember 2'-0" being the standard but I need to make darn sure.
There's a 2" open space above the beam and roof deck where the joists sits on the solid beam. I don't think that has to be sealed if I remember correctly.
Can anyone point to where I can find the requirements for baffles FM?
Yeah, fans have to be moved but this gives a good idea what we are dealing with.