I am currently designing a combined footing to support a steel concentric brace frame above. Although I am not specifically using IBC 2006 I am using an adapted version of the code.
Previously there was a thread, which discussed overturning factor of safety that can be seen here.
Basically it states that the factor of safety against overturning is already figured into the load combinations of 0.6D + 1.0W and 0.6D + 0.7E. Therefore, when I use these combinations with my loads I then conclude (resisting moments)/(overturning forces) > 1.0, (the FOS is already built into the combination when I take 0.6x(dead loads)).
To check my calculations I have decided to use the new combined footing module inside of EnerCALC. However, when calculating the resistance to overturning they are using the alternative load combinations of 1605.3.2 specifically equation 16-17 minus the live load component of this equation (0.66D +1.3W) and then asking requiring a factor of safety of 1.5 against this combination.
I don’t understand why they are using the alternative load combinations and I don’t understand why they are developing a FOS of 1.5 on top of this combination. Have I been doing this wrong or is EnerCALC incorrect with their caclulation?
Previously there was a thread, which discussed overturning factor of safety that can be seen here.
Basically it states that the factor of safety against overturning is already figured into the load combinations of 0.6D + 1.0W and 0.6D + 0.7E. Therefore, when I use these combinations with my loads I then conclude (resisting moments)/(overturning forces) > 1.0, (the FOS is already built into the combination when I take 0.6x(dead loads)).
To check my calculations I have decided to use the new combined footing module inside of EnerCALC. However, when calculating the resistance to overturning they are using the alternative load combinations of 1605.3.2 specifically equation 16-17 minus the live load component of this equation (0.66D +1.3W) and then asking requiring a factor of safety of 1.5 against this combination.
I don’t understand why they are using the alternative load combinations and I don’t understand why they are developing a FOS of 1.5 on top of this combination. Have I been doing this wrong or is EnerCALC incorrect with their caclulation?