Hi,
IBC 1805.4.2.2 requires footing ties for structures in Seismic Design Category D, E and F for site class E and F. This can be omitted if the equivalent restraint is provided by beams in the slab or the slab itself. I interpret this to mean that the tie does not have to be directly at the footing level.
I have a situation where the footing is 4-6 feet below the top slab. I have grade beams at the top of the pedestal to minimize the moments in the pedestal by distributing the shear force of a braced frame over several pedestals. Is there a limit, in terms of distance between the grade beam and footing, for footing ties as required by IBC?
Thanks
IBC 1805.4.2.2 requires footing ties for structures in Seismic Design Category D, E and F for site class E and F. This can be omitted if the equivalent restraint is provided by beams in the slab or the slab itself. I interpret this to mean that the tie does not have to be directly at the footing level.
I have a situation where the footing is 4-6 feet below the top slab. I have grade beams at the top of the pedestal to minimize the moments in the pedestal by distributing the shear force of a braced frame over several pedestals. Is there a limit, in terms of distance between the grade beam and footing, for footing ties as required by IBC?