For Gate valve,150 rating, pneumatic test with API598 and piping system pneumatic test at site

Status
Not open for further replies.

ANTRIJ

Petroleum
Jun 24, 2014
10
0
0
IN
For flanged Gate valve,150 rating for nitrogen purging , manufacture has done valve test with air as per API598 with 7kg/cm2g w.r.t bid data sheet ,there is no leakages found .However it is noticed,there is leak in valve,with pneumatic test at 13.2 Kg/cm2 (g) at site (pressure as per process line list) as per TPI(Third Party Inspection).I would like to know ,for piping system pneumatic testing to be done including valve or not.Is there any mistake in process line list for medium and test pressure.

Your help would be highly appreciated.
Thanks in advance.
 
Replies continue below

Recommended for you

Typically, the block valve is tested together with the piping to ensure the integrity of the system.
Even the Manufacturer claimed that the valve passed the leak test at 7kg/cm2 per API598, the Class 150 valve should be good up to the 20 kg/cm2 operation pressure without a leak. Right?!
 