Foundation Design For Retaining Wall

Status
Not open for further replies.

kieran1

Structural
Feb 27, 2002
178
I need to design a retaining wall which will retain 10.0m. I have a geotech report that states the N value of the soil at foundation level is 14. Can I assume a bearing capacity of roughly 10N + Overburden pressure. The soil is a Lateritic Clay and the water table is at 9.0m below ground level.

Kieran
 
Replies continue below

Recommended for you

Don't assume anything here. Go back to the original Geotech and ask for an allowable soil bearing pressure.

If he is no longer available, engage a Geotech who is available and have him give you the value. To do otherwise is to assume too much unneeded liability and is too much of a risk of public safety.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Mike is right - you know the N value at the base - what kind of soil? Clay? Sand? What is the profile for the next 10 m or so under the foundation level? If clay, does it get "weaker" (i.e., the founding level might be in a desiccated crust) or stronger - or is there a change of materials? The allowable bearing pressure would be based on a review of both the capacity (shear) and serviceability (settlement - and most likely the governing factor) limits. Then, too, you must consider the overall global stability: 1. sliding, 2. overturning, 3. allowable bearing pressure, 4. global stability of the "system".
 
Thanks I do intend to contact the geotech.This job is overseas and I'm just carrying out some prelim calcs to see what foundations are feasible and prepare a fee proposal.

The soil profile under the foundation soil is the same for about 6-7m then sandstone bedrock.
I need to get an opinon on my assumed bearing capacity of 300KN/m2 is correct. If appointed i will get the info from the geotech.

Kieran
 
I think that 300 kPa is too high - you never said if sand or clay . . . In sand you are probably talking about 150 kPa as allowable bearing pressure for 25 mm settlement - maybe 200 given that bedrock is relatively close; in clay, you are talking about 200 kPa (but need to check for settlement to see if this needs to be reduced - depends on size of footing, OCR, etc). you could probably go 300 kPa for short term transient loading.
 
thanks BigH. I will assume a larger base for the wall

Kieran
 