Hi all,
Could you please have a look at the attached sketch? I am looking for the way to design strip foundation underneath this wall. The forces are given there and are as follows:
Resultant sliding force: 10.3 kN/m
Resultant destabilizing moment about point A: 4.2 kNm/m
Vertical resultant load: 6.3 kN/m
All above doesn't include forces/moment from the strip foundation, only from walls.
Would it be okay if I were to calculate all forces about the tip of the foundation with factor 2-3? If I were to make it wide and deep enough I would get large counter force on decent eccentricity. Is there a simpler way or better approach? Should I consider the anchor?
Thank you,
Jedi
 https://files.engineering.com/getfile.aspx?folder=7338ea42-efb5-46c1-b6f1-0f8a17c33dec&file=sketch.jpg
There are a lot of good references to address the design such as Bowles.
A couple of comments though.
H acts 1/3 up the wall from the base.
Forget the anchor and use a concrete key lug below the wall.
To prevent over stressing the soil as this a very inefficient design, the base foundation length of the wall will be close to the height of the wall.
Mike McCann, PE, SE (WA)
Thank you for the reply. Please have a look at the new sketch.
I am in the situation where I can't change this design. As you can see its stem will be faced against the brickwork with a small cavity that will be filled with a concrete/grout. I assumed that this will be bonded together so the brickwork and concrete in the cavity will act on a lever arm against the overturning moment coming from the pressure that is exerted on brickwork through liquid.
I calculated all the moments about point A and the resultant forces and moment are shown. Unfortunately, I ended up with a large sliding force so now would like to have the plinth to carry on the shear force (sliding force) that the base/ground friction force can't take. The plinth is like a ring beam so my idea would be to design it to take all loads. Can I think about it as a rectangular beam in torsion? Force couple coming from the tension in the anchor and the resultant of compressive stress between toe and plinth? Here I will make it so that the bolt will take the shear force.
Thanks again,
Jed
 https://files.engineering.com/getfile.aspx?folder=22acc84d-f170-4ea8-8ad4-06fea01744e8&file=IMG_20180427_141010.jpg
and have your footing going the other way, so the soil on top is resisting overturning.
Dik
This ground level is as the top of the plinth level. Please think about it a small above ground tank that has poor existing walls (brick) and precast walls are to strenghten it. I really can't change it so am looking for a way to design the ring beam (plinth) to resist it.