Apache1
Structural
- Dec 14, 2021
- 31
Hi all, I've got a question about minimum reinforcement in concrete walls. Per ACI 318-14 Chapter 11 the minimum ratio for vertical reinforcement = .0012 and horizontal reinforcement = .002. I was running a calculation for a restrained concrete wall (10' tall basement wall) in RetainPro and the default vertical reinforcement ratio is .0018. I can manually change that to .0012 easy enough, but the program also runs the "at least one-third greater than that required by analysis" check for rebar in flexural members that is mentioned in ACI 318-14 Chapter 9.6.1.3, which is the chapter on Beams. It also checks the 200*bw*d/fy per ACI 318-14 Chapter 9.6.1.1. It got me wondering if RetainPro is being overly conservative or if I need to adjust my own calculations which use .0012 and don't run those extra checks.
- Do you all use .0012 for vertical rebar or .0018?
- Do you use different ratios depending whether the wall is cantilever or restrained?
- Do you believe that the "one-third greater" and 200*bw*d/fy checks apply to walls? That provision is in the Beams chapter in ACI, but RetainPro seems to think that it also applies to walls. I understand that walls do act as "beams" as they have a lateral load on them from the soil.
In my opinion ACI 318-14 Chapter 11 makes it pretty clear that the minimum ratio for walls is .0012 without any exceptions or further checks needed.
- Do you all use .0012 for vertical rebar or .0018?
- Do you use different ratios depending whether the wall is cantilever or restrained?
- Do you believe that the "one-third greater" and 200*bw*d/fy checks apply to walls? That provision is in the Beams chapter in ACI, but RetainPro seems to think that it also applies to walls. I understand that walls do act as "beams" as they have a lateral load on them from the soil.
In my opinion ACI 318-14 Chapter 11 makes it pretty clear that the minimum ratio for walls is .0012 without any exceptions or further checks needed.