Foundation Wall Tolerances

Status
Not open for further replies.

Greatone76

Structural
Feb 2, 2006
64
Just to make sure I'm reading ACI-117 correctly. I have a foundation wall below grade that is sitting on a footing. Since the Foundation section of ACI-117 only seems to address footings, can I move to the building section and use "4.1—Deviation from plumb
4.1.1 For heights less than or equal to 83 ft 4 in. (25.4 m) For lines, surfaces, corners, arises, and elements: the lesser of 0.3% times the height above the top of founda- tions as shown on structural drawings or ±1 in. (25 mm)." as the tolerance for the foundation wall? It specifically references from the top of foundations. Since I am building a "foundation" element what should the tolerance be? Do I simply say the footing is the top of foundation? Any advise would be great. Thanks
 
Replies continue below

Recommended for you

You should most probably use Section 3, dealing with "FOUNDATIONS", instead of Section 4 (relating to 'CAST-IN-PLACE CONCRETE FOR BUILDINGS'). I am referring to 2006 edition of ACI 117. You may check in your edition of the code, in case it is different.

 
What do I use for a plumbness tolerance for a foundation wall?
 
You have not mentioned dimensions of 'foundation wall'. It is also not clear whether it is of PC or RC? Assuming that it will be of RC, I would go for following course of action:

a. Use Section 3.1.3, and calculate allowable tolerance, taking L as total wall height below grade, in this case.
b. Also, use Section 4 and calculate tolerance again, using story height as L this time.
c. Adopt more stringent requirement of the two tolerances calculated above.

It will however depend upon whether 'foundation wall' can in fact be considered as a foundation or not? Moreover, whether it is of sufficient bearing area to transfer the superstructure loads to underneath soil or otherwise?
 