Hey all,
I'm having a problem with a GE Frame 7EA gas turbine. While running full speed no load, the exhaust spread becomes too large causing a "Combustion Alarm".
-We dissamebled the two cans that would, taking into account the exhaust twist, be in having issues. A loose secondary nozzle was found, the improperly installed gasket was replaced and the nozzle tightened.
-No smoke was noted coming out of the stack. I have included a trend of the last run that the alarm occoured in, it was at full speed no load.
-Everything seemed to be in a steady condition when suddenly the temperatures of 3 thermocouples drop causing the maximum differential to rise above the alarm limit.
-One of the thermocouples that contributed to the alarm also had an irregularity at the 6 minute mark on startup.
There is an attached powerpoint graph showing the trend from startup through shutdown (34.5 minutes).
Any ideas?
Thanks,
Carl
I'm having a problem with a GE Frame 7EA gas turbine. While running full speed no load, the exhaust spread becomes too large causing a "Combustion Alarm".
-We dissamebled the two cans that would, taking into account the exhaust twist, be in having issues. A loose secondary nozzle was found, the improperly installed gasket was replaced and the nozzle tightened.
-No smoke was noted coming out of the stack. I have included a trend of the last run that the alarm occoured in, it was at full speed no load.
-Everything seemed to be in a steady condition when suddenly the temperatures of 3 thermocouples drop causing the maximum differential to rise above the alarm limit.
-One of the thermocouples that contributed to the alarm also had an irregularity at the 6 minute mark on startup.
There is an attached powerpoint graph showing the trend from startup through shutdown (34.5 minutes).
Any ideas?
Thanks,
Carl