rockman7892
Electrical
- Apr 7, 2008
- 1,172
On our man 6500hp 4.16kV wound rotor motor (which I have posted about before) we have an 81 frequency relay. We have recently had what appears to be nusience trips on this relay. The relay I am referring to is a Multilin MIV relay that has this 81 frequency setting. The underfreucncy settings in the relay are set to 59.50Hz with no delay and the overfrequcncy setting is set to 62Hz.
This motor has run twice with no issues and after running the 5kV circuit breaker controlling the motor is racked out. The relay trips seem to be occuring when the motor is offline and sitting idle on the system.
Unfortunately when I connected to the relay to pull the event reports I accidently deleted the event reports ( I am now kicking myself) so I cannot see exactly what frequcncy the relay was at when it tripped.
The questions that I have regarding this relay are two fold:
1) What is the purpose of using this frequency relay on a wound rotor motor? Does anyone have any information as far as reasons why a frequency relay is used. The reasons I can think are that the motor will obviously slow down, and loose power.
2) Do these settings I mentioned above seem o.k.? They seem very tight for the underfrequcny but then again I have heead that you want to keep them as tight to 60hz as possible.
3) The other strange thing is that this motor is operating on a plant that is tied to the same utility point as another plant here On-Site. The two plants are tied together right now so are all operating off of the same utility transformer. On the other plant we have an idential motor with an underfrequency relay with the same setting of 59.50 hz. I would expect to see the same issue in both places however I only see it on the one motor which seems strange.