Hello Everyone,

I've a question about jounts. In particular about grooved joints. Is there something written in the NFPA13 about this.
And if so; what value is recommended for the friction loss.
But most important, is it somewhere enclosed in the NFPA 13.

Thank for your time.

Patrick
 
Replies continue below

Recommended for you

NFPA doesn't list this explicitly as a required pressure loss. Grooved pipes butt up against each other, and are therefore calculated as a single run of piping, with the pressure loss being calculated with the Hazen-Williams equation. The c factor is used to account for friction inside the pipe.

If it's a dry system, make sure the couplings have flush seal gaskets, and use the appropriate c factor to account for increased friction inside the pipe.
 