Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

FRLS Cables - Halogen content

Status
Not open for further replies.

RRaghunath

Electrical
Aug 19, 2002
1,729
What is the halogen content to be specified (that is preferrable) and why. Could some one advise please. The cables are 33kV grade.

Thanks.
 
Replies continue below

Recommended for you

rraghunath:

The choice of zero-halogen (ZH) vs not is largely one for the regulations. Typically, if you are governed by IEC codes, the European community is more in favour of ZH cables, while in North America there is less use of these cables (unless you are US military).

In any event, IEC 60754 has the test for measuring halogen content and I believe the max % concentration is 0.5%. In the US, MIL C-24643 governs and the limit is 0.2%.

As to why you would specify ZH or not depends on whether you believe that burning of these types of cables would help or hinder during a fire. There are two groups lined up opposing each other and one group says the use of PVC compounds are OK as long as the fire does not propogate, while the other group says that the use of halogen cables creates too much toxicity and smoke.

See for a pro-ZH write-up
and
for a pro-non-HZ writeup.

Reka has a good writeup for these ZH cables that does not have too much bias - see
Lots on the web but let your national regulations be a guide; seldom are they silent on the issue.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor