FRT requirements apply during the fault(usually less than 0.125 seconds), but Anti-islanding protection usually operates in the 0.2 to 2 second time frame. FRT requirements are intended to ensure that protective devices have enough current to operate, and to keep everything except the faulted portion of the system in service. Anti-islanding protection is intended to de-energize sections of the distribution grid after the section has been isolated by an upstream protective device opening.