I need full load starting torque from a 3-phase 120-208/230 motor, and want to use a soft starter (Gavazzi RSE4812-B) on a hybrid phase converter (GenTec/Baldor) to limit current on the 1-phase 240V line. Is a heftier 3-phase supply a better solution?
The phase converter is a hybrid rotary type which uses 2 phases (as single phase 240V) also connected to the load, and generates the third phase using a modified motor. It passes motor start loads directly back to the line.
The soft starter controls 2 phases using SCRs (third pole directly connected) to ramp Vmax with a Vstart setpoint to control starting torque.
At full load starting torque, won't the motor start current be the same as the DOL start current, and passed through directly to the line?