freiwill01
Electrical
- Apr 17, 2003
- 2
I'm trying to size the fuse protecting a lockout relay connected to a generator protection relay (generator rated at 13.8kV). The current design uses 14AWG wires with 30Amp fuses. Circuit is wired to a 125VDC source. When operated the lockout relay draws 6-7amps.
However as I was reviewing NEC codes section 240.4, 310.15, 310.16, I believe the right size to use is 15Amp. This sort of tells me that 30Amp is oversized.
Here are the considerations that I've received from different sources that say 30Amp fuse is okay:
1. The 14AWG wire only sees current when the lockout relay picks up during a fault. Because it's not used as a continuous current carrying wire, it does not violate NEC standard.
2. Because the lockout relay is used to protect the genearator, the oversized 30amp fuse is used to accept most short circuit faults. Even if the short circuit burns out the rely coil, it's an acceptable risk since it is used to protect the generator.
Any comments would be helpful.
Thanks.
However as I was reviewing NEC codes section 240.4, 310.15, 310.16, I believe the right size to use is 15Amp. This sort of tells me that 30Amp is oversized.
Here are the considerations that I've received from different sources that say 30Amp fuse is okay:
1. The 14AWG wire only sees current when the lockout relay picks up during a fault. Because it's not used as a continuous current carrying wire, it does not violate NEC standard.
2. Because the lockout relay is used to protect the genearator, the oversized 30amp fuse is used to accept most short circuit faults. Even if the short circuit burns out the rely coil, it's an acceptable risk since it is used to protect the generator.
Any comments would be helpful.
Thanks.