REM76
Electrical
- May 3, 2008
- 19
Can limiters be put the load side of low voltage power circuit breakers? I have alawys seen them on the line side. Is there an associated standard like NEMA or ANSI for this application. The reason that we want to put the limiters on the load side is because we are doing a retrofill job where the old breakers are old FPE breakers with fuses on the load side.
Thanks
Thanks