gilldawg79
Industrial
- Jun 7, 2007
- 4
What formula do you use to properly fuse the control circuit in a Motor Starter....480 VAC for an example.
This is the formula that I have....
Primary side: VA of control transformer .050KVA / 480 (Primary side)= Fuse size
50VA/480= .10+25% =.13 or 1/10
Fuse on Primary side should be larger due to Inrush and use a time delay fuse?
Secondary side: VA of transformer .050KVA / 120 (Secondary Side)= Fuse size
50VA/120=.42 or 4/10 or smaller .25 amp
Fuse on Secondary side should smaller than the formula with a Fast Acting Fuse?
Is this correct?
Thanks,