Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

fusing relays

Status
Not open for further replies.

angryman

Electrical
Jun 20, 2006
49
When selecting a 220vac relay, I notice that htey all have an extremely low current rating...generally around 9mA...are these generally fused? Using the max fuse size of 300X doesn't even come near the typical low fuse value of .063 (1/16a).....I'm swiching the relay on through a limit switch...
 
Replies continue below

Recommended for you

Normally the fuse is intended to protect parts of the system or equipment upstream of the fuse, not the connected load. Go with a 100mA or 250mA fuse. If the relay goes bad the fuse will blow. Very low current fuses are usually bad news because they are vulnerable to physical shock damage.


----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
Why do you think that you need a fuse at all?

Fuses are never, ever used the way you are going to use them.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
I will not use a fuse....I didn't think I ever saw one in such a situation....I was not thinking.....basically, the coils will not draw much more than 25ma....
Once again you've helped me, thanks....

Mark
 
you use a voltage style relays, and its work requirements are around 60% of 220 VAC, and over 9 ma. please check the mannual again, coz I think the contacts of the relays must can support over 5AAC, whatever is the working current ot tripping current. they are differnt, or you can try to contact the company which produces the relays.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor