In thread238-162891 advidana mentioned that "an insulator is required on the guy line from the pole to the ground for galvanic protection"
What sort of a configuration requires that?
We require insulator in guys, but I was told is was so that if the top part becomes accidently energized, the public cannot walk up and touch a hot ground wire. Also it allows workers on the pole a measure of safety if they touch something hot and the top of the guy wire. Some utilities do the opposite, requiring everything thing to be grounded so the relaying will operate faster, especially in areas where the soil is poor.
What sort of a configuration requires that?
We require insulator in guys, but I was told is was so that if the top part becomes accidently energized, the public cannot walk up and touch a hot ground wire. Also it allows workers on the pole a measure of safety if they touch something hot and the top of the guy wire. Some utilities do the opposite, requiring everything thing to be grounded so the relaying will operate faster, especially in areas where the soil is poor.