Nov 23, 2020 #1 engr2GW Petroleum Nov 7, 2010 307 0 0 US Hello, We have API 12F tanks that operate from 1 to 12 ounce/sq-inch, trying to measure the vent gas to the flare at such a low pressure, any experience with measurement device at such low pressure? As much as possible, do it right the first time...
Hello, We have API 12F tanks that operate from 1 to 12 ounce/sq-inch, trying to measure the vent gas to the flare at such a low pressure, any experience with measurement device at such low pressure? As much as possible, do it right the first time...
Nov 23, 2020 #2 LittleInch Petroleum Mar 27, 2013 21,097 3 38 GB Velocity? Accuracy needed? Could try Ultrasonic, pitot tube or hot wire. All very low or no differential pressure. Probably need at least 10 to 15 D straight length to get sone uniform flow Remember - More details = better answers Also: If you get a response it's polite to respond to it. Upvote 0 Downvote
Velocity? Accuracy needed? Could try Ultrasonic, pitot tube or hot wire. All very low or no differential pressure. Probably need at least 10 to 15 D straight length to get sone uniform flow Remember - More details = better answers Also: If you get a response it's polite to respond to it.
Nov 23, 2020 #3 Latexman Chemical Sep 24, 2003 6,923 1 38 US My past practice has been to infer the vent flow from the displacement of incoming materials into the tanks. Is that not good enough? Good Luck, Latexman Upvote 0 Downvote
My past practice has been to infer the vent flow from the displacement of incoming materials into the tanks. Is that not good enough? Good Luck, Latexman