briand2 and friartuck as stated by supaman above, the design is required to meet IFGC (International Fuel Gas Code). As such, it is not relevant how this is done in other parts of the world unless they are required to follow the IFGC. That is why I suggested he review the applicable codes. The code is very clear on the limitations, restrictions, and prohibited pipe locations for routing gas piping (section 404.1 through 404.16.) In addition, there are many other relevant code requirements discussed in Chapter 4.
Supaman, I can think of no code exceptions for material types that modifies 404.1. That is why I questioned your assumption. Keep in mind that the plenum space, above a dropped ceiling, often used for return air, is not an “air circulating duct.” However, there are many restrictions for routing pipe in concealed spaces. Read the entire Chapter on gas piping before making assumptions. Your original question about walls depends on a lot of factors listed in the code. Is it a solid wall? What protections will be provided against physical damage? Etc.