McMoe, It sounds like you are on the delivery side of the situation, and you want to know what problems you are going to cause someone like me on the recieving end. My landfill gas fuel averages about 540 Btu/scf SLHV. If it varies by more than about 5%, my fuel system can't compensate.
If it varies too high, I can adjust my fuel ratio controller parameters and keep operating, as long as the plant operator sees the change before the engine goes into detonation and shuts down. If the detonation sensing system fails, then I experience severe engine damage.
If the fuel heat content drops more than 5%, then my fuel system can't supply enough to make full power. Therefore, the plant can't produce rated output. If my power is being sold via contract or is pre-scheduled into the grid for the open market, then I have to buy replacement power. If the market is high, I am going to be real mad.
For either case, I would be on the phone to my GasCo right away to find out what is going on.
Even with pipeline fuel, assuming just under 1000 btu/scf, your 60-70 Btu change would be outside the 5% variance allowed by my engine's fuel system. Your inability to control fuel quality is going to impact your customer negatively, if his system is similar to mine.