We want to select a generator protection relay for a gas turbine starting with a Static Frequency Converter.
This relay must protect the generator during startup and normal operation.
The generator is used as a motor to start the turbine.
Once the turbine is started the generator operates as a generator.
What criteria should we use to select the generator protection relay?
The "Power System Relay Committee" gives some guidelines:
"Typical generator protection may be limited during the initial starting sequence due to poor operation or non-response at low frequencies. Multifunctional digital relay functions may deviate outside of specifications due to inability to track the lowest frequencies. Thus, they should be evaluated for performance below their specified frequency range."
IEEE standards C37.102 says:
"Curves of element performance versus frequency are often supplied by manufacturers down to some value
of frequency. Multifunction relays provide protection down to a low frequency value but if a protective
function characteristic is such that it may falsely operate at low frequencies, then it should be disabled
during starting. In some installations single function relays, with good performance at low frequency, have
been applied to provide additional protection during start-up."
There are different relays on the market some relays are able to track frequency from 3 Hz to 70 Hz other from 10 Hz to 125Hz for example.
What is the minimum frequency the relay should be able to track?
Is 10 Hz acceptable or do we need to go down to 3 Hz?
Which relays do you typically see for this application?
Can we use a standard protection relay by considering that the SFC will provide phase overcurrent, phase unbalance protection, and ground protection at low frequency?
Thanks for your help!
We want to select a generator protection relay for a gas turbine starting with a Static Frequency Converter.
This relay must protect the generator during startup and normal operation.
The generator is used as a motor to start the turbine.
Once the turbine is started the generator operates as a generator.
What criteria should we use to select the generator protection relay?
The "Power System Relay Committee" gives some guidelines:
"Typical generator protection may be limited during the initial starting sequence due to poor operation or non-response at low frequencies. Multifunctional digital relay functions may deviate outside of specifications due to inability to track the lowest frequencies. Thus, they should be evaluated for performance below their specified frequency range."
IEEE standards C37.102 says:
"Curves of element performance versus frequency are often supplied by manufacturers down to some value
of frequency. Multifunction relays provide protection down to a low frequency value but if a protective
function characteristic is such that it may falsely operate at low frequencies, then it should be disabled
during starting. In some installations single function relays, with good performance at low frequency, have
been applied to provide additional protection during start-up."
There are different relays on the market some relays are able to track frequency from 3 Hz to 70 Hz other from 10 Hz to 125Hz for example.
What is the minimum frequency the relay should be able to track?
Is 10 Hz acceptable or do we need to go down to 3 Hz?
Which relays do you typically see for this application?
Can we use a standard protection relay by considering that the SFC will provide phase overcurrent, phase unbalance protection, and ground protection at low frequency?
Thanks for your help!