Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Gas turbine sychronizing breaker opens immediately its synchronizes

Status
Not open for further replies.

Ekow123

Mechanical
Oct 2, 2013
4
Hi all,

I am a visiting engineer at frame 9e power plant.The gas turbine starts and accelerates to full speed no load and whenever they about synchronizing,the breaker closes and opens after some few seconds.

The mass flow rate of the distillate fuel fluctuates and never keeps increasing.It decreases and increases.

The main fuel pump pressure is stable and the individual pressures to the combustion canisters are also stable.

The exhaust spread is almost uniform.

 
Replies continue below

Recommended for you

If the turbine runs, the breaker opening would indicate a electrical issue when synchronising.

I don't think this is the correct forum for this question, you'll probably get a better response elsewhere.

HPost CEng MIMechE
 
You should be able to set up the control system Historian to see what is initiating the breaker closure and opening. Most can timestamp at 0.1 second intervals. Trends of key turbine data will help too, especially if cross-referenced to the software logic. What engine and controller are you using?

And yes, this is probably the wrong place for this question. Try Forum666, although the answer will likely be similar to the above.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor