I have a customer with a 60 MVA National Industri unit that had circulating current problems that caused two of the top core bolts to be eroded away and break. All 8 core bolts were replaced and positively grounded. The unit was put into service in June-07 and is once again gassing at a high rate of rise (combustibles)
Hydrogen (H2):234
Methane (CH4):198
Ethane (C2H6):41
Ethylene (C2H4):334
Acetylene (C2H2):26
Carbon Monoxide (CO):33
Carbon Dioxide (CO2):332
I did an internal and have eliminated the core bolts/tap changer and secondary bus. Furans and metals are good!
Has anyone dealt with this type of problem as it relates to a furnace transformer? Any help/suggestions would be appreciated!