A client has asked us to provide a spray cooling system for the walls of diesel fuel tanks in case of a neighbouring fire.
We have explained him that following NFPA 30 and the condition of the installation, type of tank, contents, separations, etc., a spray protection system is not a NFPA requirement. He has insisted that he wants a means to provide cooling, and that´s it. Our propposal is to desing rings of open nozzles following NFPA 13 and 15 with the respective water spray density, that can provide spray water on the sides of fire exposure of each tank.
We are used to design deluge systems with their respective deluge valve following NFPA 15 with automatic operation; but in this case, since there is plant personel and fire brigade 24 hr and we dont´t have a need to activate the cooling flow in a sudden way; I don´t see the need of a deluge valve with an automatic actuation system. Also considering that in the even of a fire, a manual valve located in a safe place would be enough to control the activation of the cooling spray on the exposed face of the tanks.
So I´m reckoning about not installing a deluge valve but only a gate valve (listed, indicating, etc.) to control the activation of the spray system manually. It keeps the system much simple and reliable. I´ve never done this and I don´t find a prohibition on NFPA to use a gate valve to control a cooling system, but I would like to hear the opinion of others on this.
We have explained him that following NFPA 30 and the condition of the installation, type of tank, contents, separations, etc., a spray protection system is not a NFPA requirement. He has insisted that he wants a means to provide cooling, and that´s it. Our propposal is to desing rings of open nozzles following NFPA 13 and 15 with the respective water spray density, that can provide spray water on the sides of fire exposure of each tank.
We are used to design deluge systems with their respective deluge valve following NFPA 15 with automatic operation; but in this case, since there is plant personel and fire brigade 24 hr and we dont´t have a need to activate the cooling flow in a sudden way; I don´t see the need of a deluge valve with an automatic actuation system. Also considering that in the even of a fire, a manual valve located in a safe place would be enough to control the activation of the cooling spray on the exposed face of the tanks.
So I´m reckoning about not installing a deluge valve but only a gate valve (listed, indicating, etc.) to control the activation of the spray system manually. It keeps the system much simple and reliable. I´ve never done this and I don´t find a prohibition on NFPA to use a gate valve to control a cooling system, but I would like to hear the opinion of others on this.