Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

GE AK-2 circuit breaker specs 1

Status
Not open for further replies.

Eleceng01

Electrical
Mar 5, 2007
174
I have tried searching Eng-Tips, and the GE website, but I haven't been able to find information for a GE AK-2-50 circuit breaker. Specifically, I am looking for the interrupting ratings of the breaker.

GE support thus far has not been of any use - they seem as lost as me.

Thank you in advance for any assistance.
 
Replies continue below

Recommended for you

The GE AK-2-50's interrupting rating depends on your system voltage and if they are equipped with direct-acting instantaneous overcurrent trip devices. Here's the breakdown.

System Voltage|Interrupting Rating w/ Instantaneous Trips
600 VAC |42,000A
480 VAC |50,000A
240 VAC |65,000A

On a system without instantaneous trips, the numbers remain the same except when the system voltage is at 240VAC. If your system voltage is at 240VAC and your breakers dont have instantaneous trips, the IC is 50,000A

Matt Brierley
Satin American Corp
 