GE FANUC PLC Password Unlock 2

Status
Not open for further replies.

Pokemon

Electrical
Dec 10, 2002
2
I would like to ask about currently having a GE FANUC Series 90-30 PLC, the problem is it already locked with password and unable to access in. I am sure there is no any method to reset the password, is there any software or any idea to unlock the password?
THANKS!
 
Replies continue below

Recommended for you

Remove the battery and short the 'super-cap' on the CPU, that will set the CPU back to factory defaults (i.e - No Password.) New CPUs label a set of solder tabs 'CLR-MEM' for this. Then download your own program without a password.
This SHOULD be the ONLY way.
 
Just a warning - the kind of factory reset described above also restores the application memory to 'factory default' i.e. empty. Make sure you have a copy of your application program before attempting this!


----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 
This also tells me that the application is not stored in a genuine flash or EAROM memory. Since lithium battery is what 8 to 10 years if the power is left on all the time I should expect to have to replace the battery. In a 1 or 2 shift per day factory where the machines are turned off expect shorter battery life.

What I have done with some of my computers is to replace the lithium cell holder with a pair of wires that go to my own battery holder and a small electrolytic capacitor so that I can change the battery without losing the setup. I have found that three 1.5 volts AA cells in series will work in place of a 3-volt lithium battery. One way to do this is to modify a 4 cell holder so that one of the slots contains the electrolytic capacitor and the other 3 slots act as a 3 cell holder.

A variation on this is to wire two 2 cell holders in parallel so that there can be overlapping battery changeout. 4 AAA cells in series parallel seems to work over say a 2 or 3 year period. Same thing would work for a critical programmable controller by hacking in 2 external battery holders.

Mike Cole
 
All 90-30 CPU's have at least 20 minustes of capacitance built in. i.e With out power the capacitors will hold the RAM for at least 20 minutes. Alternativly all 90-30 CPU's are designed that you can safely change the battery while power is connected.
 