SparkOmatix
Electrical
- Oct 26, 2010
- 29
I have a switchgear (15kV, 95kV BIL, 1200A) that feeds a 5000kVA, 15kV to 4160V transformer that in turn powers a 5kV switchgear (1200A, 60kA RMS symmetrical). The 5kV switchgear feeds to 1750HP motors. When we attempt to start one while the other is running...it runs for about 5 minutes then the GE Multilin 750 (located in the 15kV gear) trips on "Ground Time OverCurrent".
The GE 750 is set as follows:
Phase:
Phase OC PU 1.4 (420A)
Ext Inverse 6; 1 (S;M)
Phase Inst OC PU 10 (3000A)
Ground:
Ground OC PU 2 (100A)
Ext Inverse 10; 1 (S;M)
Does anyone have any thoughts? Could this be a potentially serious issue or is it more likely an unbalance and/or setting issue?
Thanks in advance!