Over the weekend, I was asked if I was interested in getting involved in setting up a network that would operate as follows:
- Primary Voltage 10kV / Secondary Voltage 400V.
- 4 substations each approximately 250metres apart.
(four corners of a square).
- Network primary AND secondary selective (fully ringed on both 10kV and 400V sides).
- Each (of 4) substation has a single fan assisted transformer.
- Network can be fed from any combination of:
o Electricity Supply Company incomer
o 2 x 2MVA 10kV Diesel Generators
(so lowest possible fault level is 1x1 MVA Generator in circuit / highest is Supply Network in parallel with both generators).
- Both primary and secondary rings closed all of the time – i.e. all transformers energised and in parallel.
Now, all of my (fairly limited) experience has been on radial networks with redundant transformers operating with open couplers / auto-transfer and primary-only ring networks with an open point and no transformer in parallel.
The type of network that I have outlined above looks horrendously complex to me (and the amount of copper that has to be run to connect a functioning ring between the four substations at the 400V level is mind-boggling).
Has anybody out there set up a network like this in the past ? Am I right in thinking that the different combinations of supply and the multiple parallel paths will make for a relay setting, discrimination nightmare ?
Or is it just that this is a configuration that i am not used to and actually is quite standard and fairly easy to implement ?
Any feedback much appreciated.
Col
Clients pay to be told what you think - not what they think (but THEY don't always think that).
- Primary Voltage 10kV / Secondary Voltage 400V.
- 4 substations each approximately 250metres apart.
(four corners of a square).
- Network primary AND secondary selective (fully ringed on both 10kV and 400V sides).
- Each (of 4) substation has a single fan assisted transformer.
- Network can be fed from any combination of:
o Electricity Supply Company incomer
o 2 x 2MVA 10kV Diesel Generators
(so lowest possible fault level is 1x1 MVA Generator in circuit / highest is Supply Network in parallel with both generators).
- Both primary and secondary rings closed all of the time – i.e. all transformers energised and in parallel.
Now, all of my (fairly limited) experience has been on radial networks with redundant transformers operating with open couplers / auto-transfer and primary-only ring networks with an open point and no transformer in parallel.
The type of network that I have outlined above looks horrendously complex to me (and the amount of copper that has to be run to connect a functioning ring between the four substations at the 400V level is mind-boggling).
Has anybody out there set up a network like this in the past ? Am I right in thinking that the different combinations of supply and the multiple parallel paths will make for a relay setting, discrimination nightmare ?
Or is it just that this is a configuration that i am not used to and actually is quite standard and fairly easy to implement ?
Any feedback much appreciated.
Col