I have a question in regards to a project I'm involved with. Specifically, this is a Wind Farm generation facility although the answer to my questions does not necessarily have to be specific to wind farms. The turbines at this particular facility are DFIG machines that are capable of supplying/consuming dynamic amounts of reactive power based on the wind farm controller's direction.
There is a need outlined that the farm must be capable of producing power at a +/- .95 power factor at the point of interconnection. The capabilities of the wind turbines will obviously be limited by the generator and the characteristics of the collector system for the wind farm.
Here is where I get confused - despite that requirement, the farm will always be operating in VOLTAGE control mode per the utility's direction. The wind farm management system will receive a voltage setpoint from the local utility and make the necessary changes to meet this voltage. The way I see it - there are two ways to do this.
A) Change the reactive power output to either boost or lower the voltage. If I understand correctly, with no other changes, producing more vars will make the generation facility more "leading," producing more capacitive VARS, and boosting the voltage at the point of interconnection. Producing less Vars will sway the farm more towards the "lagging" characteristic, consuming vars, lowering the voltage. (Induction generators, by nature, are lagging meaning that they consume Vars, or alternatively, they produce negative Vars, is that correct?)
B) You could also use the On Load Tap Changer of a transformer to meet the voltage requirement, couldn't you? If your generation facility is only operating in Voltage Control mode, doesn't the presence of an On-Load tap changer directly offset the amount of reactive compensation needed at the generation facility?
^The above is where I get confused. I'm confused at the interaction between an on-load tap changer and the reactive power support capabilities when operating a facility under voltage control mode. Anyone able to help make this more clear to me?
There is a need outlined that the farm must be capable of producing power at a +/- .95 power factor at the point of interconnection. The capabilities of the wind turbines will obviously be limited by the generator and the characteristics of the collector system for the wind farm.
Here is where I get confused - despite that requirement, the farm will always be operating in VOLTAGE control mode per the utility's direction. The wind farm management system will receive a voltage setpoint from the local utility and make the necessary changes to meet this voltage. The way I see it - there are two ways to do this.
A) Change the reactive power output to either boost or lower the voltage. If I understand correctly, with no other changes, producing more vars will make the generation facility more "leading," producing more capacitive VARS, and boosting the voltage at the point of interconnection. Producing less Vars will sway the farm more towards the "lagging" characteristic, consuming vars, lowering the voltage. (Induction generators, by nature, are lagging meaning that they consume Vars, or alternatively, they produce negative Vars, is that correct?)
B) You could also use the On Load Tap Changer of a transformer to meet the voltage requirement, couldn't you? If your generation facility is only operating in Voltage Control mode, doesn't the presence of an On-Load tap changer directly offset the amount of reactive compensation needed at the generation facility?
^The above is where I get confused. I'm confused at the interaction between an on-load tap changer and the reactive power support capabilities when operating a facility under voltage control mode. Anyone able to help make this more clear to me?