Gentlemen,
I have a plant that is serviced by a 5KV generation and distribution system. All of the loads on this system are three phase loads. If all of the generators are low resistance grounded, do I need to run a ground wire along with the phase wires from the 5KV switchgear to each of the 5KV loads (pad mounted gear, transformers, etc.) All of the loads in question will be grounded via "local" ground rods & loops.
If I do not run a ground wire with the phase conductors, is the earth an allowable return path for returning a phase to ground fault to the generator source?
I have looked in the National Electrical Safety Handbook (NESC), IEEE Std. 142, NEC and Soares Book on Grounding to shed some light or guidance, but have come away with very little.
Any guidance on this subject would be greatly appreciated.
I have a plant that is serviced by a 5KV generation and distribution system. All of the loads on this system are three phase loads. If all of the generators are low resistance grounded, do I need to run a ground wire along with the phase wires from the 5KV switchgear to each of the 5KV loads (pad mounted gear, transformers, etc.) All of the loads in question will be grounded via "local" ground rods & loops.