Various scenarios come to mind...unit trips and line trips / auto-reclosures are generally very different animals...
Picture a breaker-and-a-half type switchyard in use for a three unit 1500 MW fossil station and three export circuits, with one 500 MW unit and one export circuit per diameter. Reserve station service transformers are connected to the "upper" and "lower" busses. A 1.5 breaker scheme is also used at the remote end of the export circuits.
Say station is at full production and one export circuit sustains an automatic trip with reclosure, due to, say, a lightning strike; provided the remaining export paths can absorb the full station output in the short term without developing excessive load angle and therefore instability, there is no reason to expect them not to survive. If the generating units are equipped with quick-acting AVRs or TSECs [ transient stability excitation controllers ] there is no reason not to expect them to survive the event as well. Based on the normal time delays applied to the typical reclosure schemes I'm familiar with, the circuit is placed on potential via its under voltage plus time breaker at the remote terminal, the companion remote breaker also recloses under synchro-check supervision, then the local breakers also reclose under synchro-check supervision. Mint!
Since circuit restoration has occurred rapidly enough, no generation runback occurs, as the time delay setting in the run-back scheme has not elapsed before everything is back to normal, therefore no thermal limits have been encroached...
Planned outages to one circuit would alter this scenario considerably...and unit trips are another story entirely.
Hope I'm not being too rudimentary...
CR