davidbeach
Electrical
- Mar 13, 2003
- 9,492
A thought I've been mulling over for the past few days.
Normally where a generator and unit transformer are installed, and there is a breaker with the generator, the configuration is: Neutral Connection; Generator Windings; Generator Breaker; Transformer. In this configuration, if there is a phase-to-ground fault within the generator tripping the breaker does nothing (much) to reduce the fault current, that is done by tripping the field and prime-mover and waiting for the voltage to collapse to the point that current can no longer flow.
But what if the breaker were instead between the Neutral Connection and the Generator windings? In this case, current, to both the load and to the fault, would be interrupted. No current flow, less total damage. This is assuming that the generator is feeding a delta winding on the unit transformer, so that voltage fed back into the windings after the breaker trips would not have a path through the winding ground fault.
Certainly I'm not the first to think of this, so what am I missing? Why aren't generator breakers on the neutral side of the winding rather than the line side of the winding?
David.
Normally where a generator and unit transformer are installed, and there is a breaker with the generator, the configuration is: Neutral Connection; Generator Windings; Generator Breaker; Transformer. In this configuration, if there is a phase-to-ground fault within the generator tripping the breaker does nothing (much) to reduce the fault current, that is done by tripping the field and prime-mover and waiting for the voltage to collapse to the point that current can no longer flow.
But what if the breaker were instead between the Neutral Connection and the Generator windings? In this case, current, to both the load and to the fault, would be interrupted. No current flow, less total damage. This is assuming that the generator is feeding a delta winding on the unit transformer, so that voltage fed back into the windings after the breaker trips would not have a path through the winding ground fault.
Certainly I'm not the first to think of this, so what am I missing? Why aren't generator breakers on the neutral side of the winding rather than the line side of the winding?
David.